Well, I have my trench all dug, but at the moment I'm kind of screwed.
The NEC says you can't have more than 360 degrees in bend for conduit.
The cable has to go from the subpanel straight to the wall, 90 degree down into the ground and turns 90 degrees away from the building for a way and the bends 45 degrees left and the 45 degrees right to go around the corner of concrete pad, and then makes a 90 degree right turn at the other corner of the pad.
That's 360 degrees.
From there it continues and makes a 45 degree left, several more feet it makes another 45 degrees left (now it's at the corner of my concrete pad next to the house that I park on) and is heading for the house.
That's 450 degrees.
When it gets to the house it has to turn up 90 degrees along the house and then make a 90 degree left turn and head for the main breaker panel.
That's a total of 630 degrees.
I'm thinking I need to put a pull box in the ground where the 5th bend would be (the 3rd 90 degree bend). From here I'd have a total of 270 degrees of bends left.
The pull box is something I just became aware of. Now I have to figure out what to get, where to get it, and how to install it.